    KNX/EIB Wind Alarm Blocking (Override)

    Setup: Blind/Shutter Actuator, Weather Station, Push Button Smart Sensor (all MDT).

    At wind over the Threshold a 1 bit alarm telegram is sent to all associated Blind actuators in order to move up the blinds.

    The alarm will go off when the wind is bellow a 2nd threshold.

    As long as the alarm is on, the manual control of the blinds is disabled. I wish to be able to override the alarm from a push button of any room.

    The weather station doesn't allow blocking as for example in a presence sensor. Is there a way to implement logic or some other trick to override the alarm for a specific channel from the smart push button?

    #2
    You could filter the windalarm via an inverted And in a smal logic.
    regards Florian

    Kommentar


      #3
      Hi Florian,
      Thank you. It works!
      Regards,
      Joe

      Kommentar


        #4
        Great

        Kommentar