My EibPC became selective on the telegrams captured from the bus since I downloaded a new application program yesterday.
I've taken two screen-shots (one from EibStudio and another one from ETS3 logs), clearly showing that the response GA 4/2/100 coming from source address 1.1.7 after launching request GA 4/2/0 (from EibPC) is not captured by the hardware. The internal EibState for 4/2/100 still shows ON, which is corrected after manually reading the value from the bus. Note that the first read response is also not captured, a second attempt recovers the situation.
The problems is there for multiple GAs and physical devices, so problem clearly resides in the EibPC which is connected via FT1.2 to the bus since 6 months now. The occurrence seems higher for GAs at the upper part of the hauptgruppen list, however this be a coincidence as I've more dynamic elements in there (temperature updates, heating control, ...).
The problem started when adding some code that seems to blow up the usage% across the (magic?) 10% barrier, I reached 11.1% now. I remember that some months ago a problem had been solved when reaching 12% -> could this one be related?
I'd also like to mention that I've noticed telegrams being lost during start up - particularly when a lot of ToggleButton makros are sending their read request. I assumed this was due to internal queue overflows and didn't raise a ticket for that before.
Usage EibPC 11.1 %.
EibParser ended without errors.
(c) 2008-2010 Enertex Bayern GmbH
www.enertex.de
% C:/bin/Eib/nconf -i 192.168.1.6
IP-Address of EibPC: 192.168.1.6
Firmware Version of EibPC: v1.308
Serial of EibPC: 00000209
Netzwerkeinstellungen: DHCP
Netzmaske: 255.255.255.0
Gateway: 192.168.1.1
Nameserver 1: 192.168.1.1
Nameserver 2: ?
Nameserver 3: ?
Patches:
1.000.ptc
1.001.ptc
1.002.ptc
1.003.ptc
1.004.ptc
1.005.ptc
1.006.ptc
1.007.ptc
1.300.ptc
1.301.ptc
1.302.ptc
1.303.ptc
EIB-Interface: FT1.2
I've taken two screen-shots (one from EibStudio and another one from ETS3 logs), clearly showing that the response GA 4/2/100 coming from source address 1.1.7 after launching request GA 4/2/0 (from EibPC) is not captured by the hardware. The internal EibState for 4/2/100 still shows ON, which is corrected after manually reading the value from the bus. Note that the first read response is also not captured, a second attempt recovers the situation.
The problems is there for multiple GAs and physical devices, so problem clearly resides in the EibPC which is connected via FT1.2 to the bus since 6 months now. The occurrence seems higher for GAs at the upper part of the hauptgruppen list, however this be a coincidence as I've more dynamic elements in there (temperature updates, heating control, ...).
The problem started when adding some code that seems to blow up the usage% across the (magic?) 10% barrier, I reached 11.1% now. I remember that some months ago a problem had been solved when reaching 12% -> could this one be related?
I'd also like to mention that I've noticed telegrams being lost during start up - particularly when a lot of ToggleButton makros are sending their read request. I assumed this was due to internal queue overflows and didn't raise a ticket for that before.
Usage EibPC 11.1 %.
EibParser ended without errors.
(c) 2008-2010 Enertex Bayern GmbH
www.enertex.de
% C:/bin/Eib/nconf -i 192.168.1.6
IP-Address of EibPC: 192.168.1.6
Firmware Version of EibPC: v1.308
Serial of EibPC: 00000209
Netzwerkeinstellungen: DHCP
Netzmaske: 255.255.255.0
Gateway: 192.168.1.1
Nameserver 1: 192.168.1.1
Nameserver 2: ?
Nameserver 3: ?
Patches:
1.000.ptc
1.001.ptc
1.002.ptc
1.003.ptc
1.004.ptc
1.005.ptc
1.006.ptc
1.007.ptc
1.300.ptc
1.301.ptc
1.302.ptc
1.303.ptc
EIB-Interface: FT1.2
Kommentar