    Siemens 5WG1 260-4AB23 issue

    Guten Morgen zusammen,
    I try to add new Siemens 5WG1 260-4AB23 to my project. The physical address was assigned without any problems but when I try to download application program and group addresses, the process fails with Dawnload failed error - The device does not respomd in appropriate time. Meantime I checkd bus during programm process and see no communication issue. The 260-4AB23 (phy.addr. 1.1.8) sends the T_Disconnect at the end of download process:
    #,Time,Service,Flags ,Prio,Source Address,Source Name,Destination Address,Destination Name,Rout,Type,DPT,Info
    186,4/18/2020В 11:16:36.425 AM,from bus,,System,1.1.8,Binary Input RL 260/23,1.1.125,-,6,PropertyValueResponse (S=4),,"ObjectIndex=4, PropertyId=5, Count=1, StartIndex=1, Data=$01"
    187,4/18/2020В 11:16:44.207 AM,from bus,,System,1.1.8,Binary Input RL 260/23,1.1.125,-,6,T_Disconnect,,
    No other issues in this project with programming or operations.

    The only reason of issue I can imagin is either broken 260-4AB23 or wrong application programm.

    I used SIEMENS Gamma Firmware download tool and upgraded firmware from V01 to last availaible V03. No problem with communication with 260-4AB23 in this tool. This tool shows 260-4AB23 parameters as follows:
    OS version 10 43
    Order number 5WG1 260-4AB23
    Mask 07B0
    Manufacturer Siemens
    KNX Serial number 00 01 00 3D 33 60
    Hardware ID 00 00 00 00 00 66
    HAL version 00 16
    FW version 00 16
    Expanded device type 05 8A 00 01 00 02 00
    Device type 05 8A 00 01 00 80
    Build Revision 00 00 39 BF
    But firmware upgrade didn't resolve my issue.

    I use knxprod file from the SIEMNS site. The application program is 07 B0 S4 Ein-Aus-Um/Dim/Jalo/Wert/Zykl 983101.
    The ETS version is 5.5.2 (build 665).

    Any comments and ideas are very appreciated.

    Thank you in advance.

    Best regards,
    Murr


    #2
    Your ETS is rather old. The current version is 5.7.4.

    Kommentar


      #3
      Which interface do you use? I have several problems with non siemens interfaces like TP-UART with knxd or ABB-USB. After switching to siemens IP interface there are non more problems anymore.

      Kommentar


        #4
        Zitat von Klaus Gütter Beitrag anzeigen
        Your ETS is rather old. The current version is 5.7.4.
        Hi Klaus,

        The upgrade to ETS 5.7.2 (Build 7.4.3) resolved the issue.

        Thanks a lot!

        Best regards,
        Murr

        Kommentar


          #5
          Zitat von tobiasr Beitrag anzeigen
          Which interface do you use? I have several problems with non siemens interfaces like TP-UART with knxd or ABB-USB. After switching to siemens IP interface there are non more problems anymore.
          Hi,

          I use Weinzierl BAOS 771.

          Best regards,
          Murr