    Zitat von SebastianFey Beitrag anzeigen
    If you can see the status group address in the group-monitor (do you?)
    Yes. I'm not very handy with the group-monitor. To do the test, I first switch on the lamp by pressing the PB once. Then I start the group-monitor and I issue an "All-Off". I can see the status GA, so I guess the actuator is duly sending it's status
    Zitat von SebastianFey Beitrag anzeigen
    you should stop looking for the problem on the actuator site.
    OK. So far, I was comparing a working and a non-working situation. I've no better method.
    Zitat von SebastianFey Beitrag anzeigen
    How does the switch look like, please post a screenshot of the associations and the parameters.
    I attached 2 files. The associations are already in a previous post
    I can't see much from those screenshots. Maybe you can ?

    About the previous picture, is it normal to see a flag set in one view and not set in another view of the same device, quite disturbing.

    What would be the right set-up of the group-monitor in order to troubleshot my problem ? I'm more used with a network monitor where I can easyly start/stop and filter upon criteria.

    Thank you for your patience.
    Angehängte Dateien

    Einen Kommentar schreiben:


  • SebastianFey
    Ein Gast antwortete
    If you can see the status group address in the group-monitor (do you?) you should stop looking for the problem on the actuator site. How does the switch look like, please post a screenshot of the associations and the parameters.

    Einen Kommentar schreiben:


  • Warichet
    antwortet
    Zitat von SebastianFey Beitrag anzeigen
    GA is not the sending one
    Still no joy.
    I'm checking your recommendations again, one by one.
    I'm puzzeled by the pictures below.
    On GA 0/0/17, "Spot On", the "S" flag of actuator 1.1.154 KO 18, IS set
    On GA 0/0/18, "Spot Status", the "S" flag of actuator 1.1.154 KO 18, IS NOT set

    I'm confused .... or is this an abnormal situation ?
    Angehängte Dateien

    Einen Kommentar schreiben:


  • Warichet
    antwortet
    Zitat von SebastianFey Beitrag anzeigen
    If the write-flag of the toggle-buttons GO were you have connected the status GA is not set, the internal state will never be updated from outside
    Thanks, that is the explanation I was missing.

    Does the above explanation hold true for a virtual Push-Button, I mean a Visu Push-Button ? No, I guess ... ?

    Einen Kommentar schreiben:


  • SebastianFey
    Ein Gast antwortete
    Zitat von Warichet Beitrag anzeigen
    I checked with the monitor, seems OK.
    If you see the status sent in the group-monitor you can obviously exclude problems concerning the actuator not sending any status.

    Zitat von Warichet Beitrag anzeigen
    --GA is not the sending one
    Don't undestand, can you elaborate a bit, please ? How can I check it ?
    A groupobject can only send to one GA. The first connected GA is the sending GA and marked by a "S" in the sending-column. By rightclicking a GA you can set it as sending.

    Zitat von Warichet Beitrag anzeigen
    --the listening object of the toggle-switch does not have the write-flag set
    Don't undestand, can you elaborate a bit, please ? Are the push-buttons involved ?
    The push-button is absolutely involved. The very root of the problem is, that the internal state of the toggle-button is wrong. Example: You press the toggle-button and it sends a "1" - the light goes on. The next time you press it it will send a "0" because it knows the light is on. If the light is now turned off by another GA (most likely a central GA) which is not connected to the toggle-button the internal state of the toggle button is wrong and on the next press it will send a "1" but nothing happens. Only at the next press you will get the desired "0". So you need to make sure, that the toggle-button gets a state update if the lights state changes.

    If the write-flag of the toggle-buttons GO were you have connected the status GA is not set, the internal state will never be updated from outside but only by the buttons application program itself when the button is pressed.

    Einen Kommentar schreiben:


  • Warichet
    antwortet
    Hi Sebastian,

    Thanks for the quick and detailed reply.
    Zitat von SebastianFey Beitrag anzeigen
    - the status isn't sent by the actuator
    Don't think so. Other channels of the same actuator are OK. I checked with the monitor, seems OK.
    Zitat von SebastianFey Beitrag anzeigen
    GA is not the sending one
    Don't undestand, can you elaborate a bit, please ? How can I check it ?
    Zitat von SebastianFey Beitrag anzeigen
    transmit-flag is not set
    The transmit-flag of all actuator's status KO are set. I compared the working and non-working devices, no obvious difference.
    Zitat von SebastianFey Beitrag anzeigen
    the actuator does not actively send on its status-object
    Don't think so. Other channels of the same actuator are OK. I checked with the monitor, seems OK.
    Zitat von SebastianFey Beitrag anzeigen
    the listening object of the toggle-switch does not have the write-flag set
    Don't undestand, can you elaborate a bit, please ? Are the push-buttons involved ?
    Zitat von SebastianFey Beitrag anzeigen
    the listening object of the toggle-switch does not care about telgrams written to it.
    Don't think so. Other channels of the same actuator are OK. I checked with the monitor, seems OK.
    Zitat von SebastianFey Beitrag anzeigen
    coupler or topology problems
    Don't think so, all participants of this GA are on the same line.
    Zitat von SebastianFey Beitrag anzeigen
    some other reason that i forgot to mention
    Maybe you'll remember ...

    Einen Kommentar schreiben:


  • SebastianFey
    Ein Gast antwortete
    there could be several reasons for this:

    - the status isn't sent by the actuator
    --- GA is not the sending one
    --- transmit-flag is not set
    --- the actuator does not actively send on its status-object but expects another device to read from there. this may or may not be changed by a parameter

    - the listening object of the toggle-switch does not have the write-flag set

    - the listening object of the toggle-switch does not care about telgrams written to it. This is seldom but some application programs do only update the internal state of a toggle-switch, if the status is written to the explicit status-object of the switch. Most of the application programs also use a write to the switch object to update its state.

    - coupler or topology problems

    - some other reason that i forgot to mention

    Einen Kommentar schreiben:


  • Warichet
    hat ein Thema erstellt KNX/EIB Double push after "All Off".

    Double push after "All Off"

    Hi,

    I'm having the classical problem where I have to push a Push-Button twice after an "All-Off" command.

    In many cases (green), this is solved by adding the actuator's status feedback GA to the actuator's switch object (hearing address)
    In one instance (red), this doesn't work. I seem to remember a post about this particular topic, where it was a flag problem, can't find it back.

    0/0/17 actuator switch GA
    0/0/18 actuator status GA
    0/7/6 All-Off GA

    Thanks for any hint.

    PS: it has been said that there should only be 1 object with the Read flag per GA. Is this a mandatory rule ?