Problems with a DALI/KNX system
    DALI Problems with a DALI/KNX system
    Sorry, but i didn't find an english section in the forum.
    1.Introducing
    I am experiencing some problems with a KNX/DALI building.
    The main goal is to control the brightness with presence detection via Dali Ballasts.
    The main relevant equipments are the following
    - Gateway KNX/DALI Siemens 141-1AB02
    - Presence detector Siemens 258-2AB21
    - Brightness Controller Siemens 255-4AB11
    The areas that must be illuminated are open-spaces from several floors.
    The open-spaces are divided in small groups of 4 Dali ballasts each, and those ballasts being controlled by a Presence Detector and a Brightness Controller, like the following schematic:
    2.Behaviours
    The system was commissioned and it is running for some months.
    The lights seems to increase and decrease to maintain a predefined brightness setpoint.
    But now I am receiving a lot of complaints of the users of those open-spaces.
    They say me that some of the lights randomly doesn’t turn on when it supposed to do.
    I have in a touch screen the option to block/unblock the detectors and turn all the lights
    on or off manually.
    3.Tests
    To understand the problem I tested with the following procedure:
    - In touch screen I blocked all the sensors and turn off the lights manually, so
    everything is turned off and the sensors doesn’t send any telegrams.
    - Next, in the touch screen, with all the lights off, I unblock the sensors so they
    could control the light themselves.
    - Next I walk in each area to trigger the sensors, and they turn on and start
    regulating to the desired setpoint (with some exceptions).
    - Next I move away from the sensors to observe the behaviour.
    What I observed:
    Generally each group of 4 ballasts turn on with the sensors, but after a while (random
    time) some ballasts of a group turn off.
    Example (see picture on first page):
    - The presence detector 2.3.9 (with a Turn-Off time of 3minutes) detects presence
    and the brightness controller starts controlling the ballasts nº31, 34, 38, 42.
    - But after, for example 30seconds (random time), the ballasts nº 31, 34 turn OFF
    for no reason, and the nº38 and 42 remains ON.
    - It isn’t the same ballasts that turn OFF every time, it could be only 1 or 3 ballast
    of the group, or even sometimes it works correctly with all lights ON.
    All the Dali groups were tested and are correct!
    Had anyone experienced this in DALI systems before ?!
    Thank you