More than 1 group addresses?

Einklappen
X
 
  • Filter
  • Zeit
  • Anzeigen
Alles löschen
neue Beiträge

    KNX/EIB More than 1 group addresses?

    Hi.

    I have a KNX presence detector (theben Sphinx 331) that I use to light up a room. I've added the 'switch on motion' object to another group address but this never gets updated. Can't I use more than 1 group address for the 'switch on motion' object?

    I have the same problem on the binary inputs. What am I doing wrong?

    #2
    Hi Mike

    It can only send to one Group Address, but it may listen to more than 1. That's a general KNX behavior.

    Cheers!
    Martin

    Kommentar


      #3
      kropfm,

      Thanks for the reply.
      So... what should be the proper implementation if I want a sensor to light up a room but I also want to monitor it's state?

      Kommentar


        #4
        well you may use the status object of your switch actuator. Or simply listen to your switch on motion Group Address.

        Kommentar


          #5
          Thanks!

          I'll do that