I do not see any difference in your Points 1) and 2). Basically, there are three methods:
1. Zweipunktregelung (don't know the english word...):
If the temperature is too low, the heating valve opens completely. There is a hysteresis setting to reduce the numer of switching cycles.
2. Closed loop regulation with direct switching of valve:
Here the valve (e.g. its acutator) will receive the command ON/OFF from your (Merten) RTR. So the settings for the PWM will be done in the RTR.
3. Closed loop regulation with PWM generated by acutator:
The RTR sends a 0-100% command to the actuator which will then do the Pulse Width Modulation.
Methods 2 and 3 will result in the same bahaviour of the valve, but 3 has the advantage that you can display a continuous signal in you visu. In addition, you will probably generate a litte less bus traffic (but needn't be).
I think there have been trys to increse the PWM base frequency such that the valve will be more or less standing somewhere in between open and close, but for my opinion, this is of no use...