Sorry for the English, I find automatic translation awful for native speakers.
Planning my installation I have put the following question to the forum: Is it possible to use standard backup PSU?
https://knx-user-forum.de/forum/%C3%...h-power-supply
I have gone forward with this setup over a year ago and thought this could be of use.
In case any of you want to create such a setup, this really works very well:
2 Meanwell PSC-100B (80€)
2 chokes from Siemens (80€)
2 12v 7aH batteries (40€)
3 swithes 3*2 poles (7 €)
I also have an extra choke for redundancy purposes.
I have an installation with 80 plus devices, divided over two lines, which communicate through a bus coupler
So, one power supply has its output connected to 2 chokes (1 for each line in my home) and it is further used to power my unchoked line (Weatherstation, etc).
It is connected to the batteries (connected in series for 24v)
The other PSU is just waiting for a disaster (but ready to be switched on).
Both PSU are connected to the switches, in a way that only one can be connected at any time.
Switch 1 cuts AC power/turns on power to PSU-A or PSU-B
Switch 2 cuts DC power/turns on power from PSU-A or PSU-B
Switch 3 cuts backup battery/turns on backup for PSU-A or PSU-B
Anyone can disconnect and reconnect or change PSU. No need for me to do that, giving time to arrange for a repair without disrupting the installation.
Power failures have no effect, the KNX BUS goes on working and you may use the binary outputs from the PSU to report AC or battery failures.
Have this system in place for over a year now, without problems.
Hope it helps someone!
Cheers
Planning my installation I have put the following question to the forum: Is it possible to use standard backup PSU?
https://knx-user-forum.de/forum/%C3%...h-power-supply
I have gone forward with this setup over a year ago and thought this could be of use.
In case any of you want to create such a setup, this really works very well:
2 Meanwell PSC-100B (80€)
2 chokes from Siemens (80€)
2 12v 7aH batteries (40€)
3 swithes 3*2 poles (7 €)
I also have an extra choke for redundancy purposes.
I have an installation with 80 plus devices, divided over two lines, which communicate through a bus coupler
So, one power supply has its output connected to 2 chokes (1 for each line in my home) and it is further used to power my unchoked line (Weatherstation, etc).
It is connected to the batteries (connected in series for 24v)
The other PSU is just waiting for a disaster (but ready to be switched on).
Both PSU are connected to the switches, in a way that only one can be connected at any time.
Switch 1 cuts AC power/turns on power to PSU-A or PSU-B
Switch 2 cuts DC power/turns on power from PSU-A or PSU-B
Switch 3 cuts backup battery/turns on backup for PSU-A or PSU-B
Anyone can disconnect and reconnect or change PSU. No need for me to do that, giving time to arrange for a repair without disrupting the installation.
Power failures have no effect, the KNX BUS goes on working and you may use the binary outputs from the PSU to report AC or battery failures.
Have this system in place for over a year now, without problems.
Hope it helps someone!
Cheers