    Hi,

    Someone has a practical experience with the Elsner TH-UP Basic ?

    In the bathroom, I've a push-button to switch on a ventilator. The ventilator has 2 speeds, this is done via 2 separate channels of a standard actuator (not a fan coil).

    Now, I've installed the TH-UP Basic to automate the process.
    I've configured humidity threshold 1 as 70% and threshold 2 as 85%
    When the threshold 1 is reached, the ventilator switches on at speed 1 (low)
    When the threshold 2 is reached, the ventilator switches on at speed 2 (high)
    This seems to work, but once the ventilator is running, it doesn't stop anymore . It's probably due to a bad setting of the hysterisis, I've RTFM but this doc is of no help, just showing the same text as in ETS, not a word of explanation about hysterisis. I've tried several values, no luck.

    Would some one be so kind to post a working example, please ?

    Thank you.

    Pic1 shows the setting of the TH-UP, GA 0/6/169-175 are for the display in the Visu. GA 0/6/21 is the actuator channel switching the ventilator On/Off, GA 0/6/23 is the actuator switching the ventilator Low speed/high speed.
    Pic2 shows the treshold setting.
    Pic3 shows channel A & B of the actuator (A=On/Off, B=Low/High speed)
    Angehängte Dateien

    #2
    Zitat von Warichet Beitrag anzeigen
    It's probably due to a bad setting of the hysterisis ... I've tried several values, no luck.
    Dear Raymond,

    what is the humidity in your rooms? I could imagine that it is hot in your place (and perhaps humid) and so inside the (colder) rooms it should be getting rather wet? What I can see in your screenprints that the ventilator should switch off at 50 % rel. humidity (for setpoint 1). It could be that in your special living condition, it would never reach this point.

    I would rather recommend to make this value much lower (say 10 % or 1 % for testing purposes). You cold as well make a plot where one could see the humidity and the status (setpoint 1, 2), so it could be decided if this is a settings' problem or an environmenal issue.

    Best regards,

    Stefan

    EDIT: I just saw the field "Humidity output sends on " change to 1 and ...
    Perhaps it doesn't send 0 - I'll see if I can find the manual.
    Mein Sammelsurium: TS2, Zennio Z38, Siemens LOGO!, Medeodata 140 S, Weinzierl KNX ENO 620, Eibmarkt IP Router, MDT KNX IP IF, Wiregate, Node-Red mit KNX Ultimate, MDT Smart II, diverse Aktoren verschiedener Hersteller ...

    Kommentar


      #3
      ... I checked the handbook (at least of the none-basic version) and you should put the setting on "• on change and periodically" or just "on change" - I think you just don't get the 0.

      Cheers,

      Stefan
      Mein Sammelsurium: TS2, Zennio Z38, Siemens LOGO!, Medeodata 140 S, Weinzierl KNX ENO 620, Eibmarkt IP Router, MDT KNX IP IF, Wiregate, Node-Red mit KNX Ultimate, MDT Smart II, diverse Aktoren verschiedener Hersteller ...

      Kommentar


        #4
        Hi Stefan,

        Thank you for the prompt reply
        Zitat von lobo Beitrag anzeigen
        what is the humidity in your rooms?
        For the moment, usually between 55-60%

        Zitat von lobo Beitrag anzeigen
        What I can see in your screenprints that the ventilator should switch off at 50 % rel. humidity (for setpoint 1).
        ?!? How do you come to this conclusion ?
        is it simply the setpoint - hysterisis ?
        so, 70-20=50% ?
        Rhâ, didn't try that combination

        Zitat von lobo Beitrag anzeigen
        It could be that in your special living condition, it would never reach this point.
        Indeed, you are right.

        Zitat von lobo Beitrag anzeigen
        I would rather recommend to make this value much lower (say 10 % or 1 % for testing purposes).
        OK
        Or, maybe the other way around: if I want 70%; I should set setpoint 1 at 75 and the hysterisis at 5, does it make sense ?


        Zitat von lobo Beitrag anzeigen
        I'll see if I can find the manual.
        You call "that" a manual ? . Maybe you have a "real" manual ? with some explanations ? All I've got is a collection of ETS PrintScreens

        Thank you for the hints

        Kommentar


          #5
          Zitat von Warichet Beitrag anzeigen
          You call "that" a manual ? . Maybe you have a "real" manual ?
          Well, this they call a manual. It is a typical example for someone only describing what one sees, but not explaining where things come from and how the user should proceed ...

          Zitat von Warichet Beitrag anzeigen
          For the moment, usually between 55-60%
          That's what I expected...

          Zitat von Warichet Beitrag anzeigen
          is it simply the setpoint - hysterisis ?
          so, 70-20=50% ?
          Rhâ, didn't try that combination
          ... this was probably too easy
          I mean, you can set the behavior at "Output is at (TV = humidity threshold value)" where you have the options:
          • TV above = 1 | TV – Hyst. below = 0
          • TV above = 0 | TV – Hyst. below = 1
          • TV below = 1 | TV + Hyst. above = 0
          • TV below = 0 | TV + Hyst. above = 1

          and if you choose the first option it is as you stated.


          Zitat von Warichet Beitrag anzeigen
          Or, maybe the other way around: if I want 70%; I should set setpoint 1 at 75 and the hysterisis at 5, does it make sense ?
          That sounds reasonable. Perhaps it would be an idea to add some time for the switching delay (at least for 1 to 0) to be sure that the ventilator will not start quickly after it stopped (what could happen with a very little hysteresis).

          But remember to put the value of "Value of parameter “Humidity switching output sends”:" to "on change" or to "on change and periodically".

          Hope it helps.

          Cheers,

          Stefan
          Mein Sammelsurium: TS2, Zennio Z38, Siemens LOGO!, Medeodata 140 S, Weinzierl KNX ENO 620, Eibmarkt IP Router, MDT KNX IP IF, Wiregate, Node-Red mit KNX Ultimate, MDT Smart II, diverse Aktoren verschiedener Hersteller ...

          Kommentar


            #6
            Hi, Stefan,

            I followed your recommedations, and it works fine now (must be pure coïncidence )
            Zitat von lobo Beitrag anzeigen
            Perhaps it would be an idea to add some time for the switching delay (at least for 1 to 0) to be sure that the ventilator will not start quickly after it stopped (what could happen with a very little hysteresis).
            Indeed, I've done it that way

            Thanks a lot