Wenn dies dein erster Besuch hier ist, lies bitte zuerst die Hilfe - Häufig gestellte Fragen durch. Du musst dich vermutlich registrieren, bevor du Beiträge verfassen kannst. Klicke oben auf 'Registrieren', um den Registrierungsprozess zu starten. Du kannst auch jetzt schon Beiträge lesen. Suche dir einfach das Forum aus, das dich am meisten interessiert.
I'm putting a Maxbotix sensor to work.
I need some guidance to correctly configure the AE/A 2.1. ABB's Tech Sup declinded to help
Given is the following information.
The AE/A is connected to an ultrasonic sensor, connected to a +5VDC supply, with an analog output 0-5V
The sensor is from MaxBotix, model LV-MaxSonar-EZ4, ref. MB1040, MaxBotix Ultrasonic Sensors, High Performance Distance & Proximity Sensors
range from 6-inches out to 254-inches (6,45-meters) with 1-inch resolution.
The application is to measure the fuel level in a tank, the sensor is placed at 1,72m from the bottom.
The sensor scale factor: Vcc/512 = mV/inch, i.e.
5/512 = 9,765625 = 9,77mV/"
1,72m = 67,7" = 661,2mV max output voltage, hence we can select the range 0-1V in the setup of the AE/A
Configuration of the AE/A 2.1 in ETS:
•A General
•Sensor type: Current/Voltage/Resistance
•Sensor output: 0-1V (soit 102,4" = 2,60m = 1V)
•Lower limit: 0
•Output value: 0
•Upper limit: 26 (1,72/2,60 = 66%) 67,7/102,4 = 66%)
•Output value: 172
•Factor: 0,01
•A Treshold value 1: lower 20, upper 30
•A Treshold value 2: lower 132, upper 142
Is this the correct configuration ?
So far, I've configured a treshold to generate an alert when the fuel level reaches low
How should I handle the sensor's dead zone, i.e. 0-6inch = 6 inch ?
I'm putting a Maxbotix sensor to work.
........................
Thank you for your comments
Hello Warichet,
as far as I found out the sensor's price is about €34.- How is your first impression of the sensor? What do you say about the quality?
I like the price!
Regards from Spain
Claus
if you make something idiot-proof, they start making better idiots......
KNX:3 Linien,121 Teiln.,Siemens N146 und N350E,RasPi mit SV,8 FBH-Kreise mit Siemens HK-Regler,HS4, Haus ohne öffentl. Wasser-/Stromversorg.,PV-Anlage Wechselrichter:SI5048(8kW, 24 Pufferbatterien 1400Ah),PV-Module mit 7,5kWp
if you make something idiot-proof, they start making better idiots......
KNX:3 Linien,121 Teiln.,Siemens N146 und N350E,RasPi mit SV,8 FBH-Kreise mit Siemens HK-Regler,HS4, Haus ohne öffentl. Wasser-/Stromversorg.,PV-Anlage Wechselrichter:SI5048(8kW, 24 Pufferbatterien 1400Ah),PV-Module mit 7,5kWp
- How is your first impression of the sensor? What do you say about the quality?
Well, the first impression is fine, although I'm still testing the sensor, not yet into production, so I'll wait before I make a definite comment. I was surprised by the size, the sensor is really small.
The quality is fine, but, after contacting TechSup for another issue, I learned that the model MB1040 is not recommended for fuel. I didn't see the info in the data sheet :-( A bit frustrating to get the info when it's too late.
About accuracy, the specs say +/- 1 inch, my measurements, although not scientific, show a bit more then 1 inch, but it's fine for my application. The main benefit is the very narrow beam, needed in my case (narrow tank).
Also, the supply is 5VDC, a bit anoying, I had to build a DC converter (7805). Current loop is more simple.
How is your first impression of the sensor? What do you say about the quality?
I've spend some time adjusting and calibrating the MB1040 together with a ABB AE/A 2.1
I've done the tests in an office environment, simulating exactly the fuel tank.
I've been piling up/removing carton boxes to simulate different fuel levels.
My conclusions are:
the device is quite reliable and accurate, although I observed measured values slightly outside the specs, but no problem for my application.
I've put the device into production, and got a very bad surprise
the sensor says: 0,40m
measured: 0,49m
This is NOT a setup problem as it worked perfectly well in an office environment. To me, it looks like the sonar beam is detecting the fuel level too soon, hence it is inapropriate for my application.
According to TechSup
Other reasons that may cause target inaccuracy is in the LV-MaxSonar-EZ sensors are: Temperature Compensation, Target Size Compensation, or the Sensor calibration itself.
So, those low cost sensor don't compensate for target size, this might be the problem. Awaiting a recommendation to buy another device.
Grmbl
Hmm, very unsatifying, though I'm still in the same "trap" still - first I chose the expensive one and failed..
I have some tests running but please don't expect results within the next 12 months - US looks very promising, but I'll never recommend anything again that hasn't worked at least 6 months here
I've put the device into production, and got a very bad surprise
the sensor says: 0,40m
measured: 0,49m
The difference can be caused by the different speed of sound in different athmosphere. You checked it out in plain air, but above the fuel level, you have another athmosphere with a slightly different speed of sound.
If you compensate the result by the factor 1,225 (0,49/0,4=1,225) the results for other hights might be right again.
The difference can be caused by the different speed of sound in different athmosphere. You checked it out in plain air, but above the fuel level, you have another athmosphere with a slightly different speed of sound.
Indeed, that's what I've been told by TechSup, but a difference of 20% on a length of 49cm, isn't that a bit much ?
If you compensate the result by the factor 1,225 (0,49/0,4=1,225) the results for other hights might be right again.
I thought about it for a while, but your suggestion implies the deviation is linear, I mean, a steady percentage, independent of the length.
Implementing the trick is no problem, as I use the HS already to calculate the fuel height (the sensor measures only the air above the fioul, not the fuel height).
thinking about it, you must measure the highest position and the lowest and set them as the limits in your analoge input. Then you should get better results.
The difference can be quite substantial, in 20°C Air, the speed is 343 m/sec, in Helium 970m/sec,
in oil(liquid) 1340m/sec.
Oil-Dust is not listed.
Wir verarbeiten personenbezogene Daten über die Nutzer unserer Website mithilfe von Cookies und anderen Technologien, um unsere Dienste bereitzustellen. Weitere Informationen findest Du in unserer Datenschutzerklärung.
Indem Du unten auf "ICH stimme zu" klickst, stimmst Du unserer Datenschutzerklärung und unseren persönlichen Datenverarbeitungs- und Cookie-Praktiken zu, wie darin beschrieben. Du erkennst außerdem an, dass dieses Forum möglicherweise außerhalb Deines Landes gehostet wird und bist damit einverstanden, dass Deine Daten in dem Land, in dem dieses Forum gehostet wird, gesammelt, gespeichert und verarbeitet werden.