    #76
    Zitat von HartmutB Beitrag anzeigen
    Caught in action !


    Zitat von HartmutB Beitrag anzeigen
    Of cause, you must specify the ordered 16m in the converter. Then it is working perfectly: If you multiply all measured values with 16/14=1,14 you have almost exactly the wanted values.
    Ok, I'll do my homework again.
    If I understand well, an alternative could be to specify the "Upper measuring limit in x % from the upper limit of effective range", i.e. that is: 14m is 87,5% of the max (16m)
    Right ?

    Zitat von HartmutB Beitrag anzeigen
    For the empty pit: Move to Germany, then you won't have *this* problem
    Well, I just moved to France
    I know Germany for having worked there many times. Besides the wheather (no thanks) I also remember the "Apfelwein" ... ouch

    Kommentar


      #77
      Zitat von HartmutB Beitrag anzeigen
      I'd give it a try with the proposed cabeling.
      So, I've re-done my homework.
      Your proposed cabling works fine.
      One thing I noticed with your cabling, the AE/A is almost immediately operational after switching on the PS (as opposed to a delay of several minutes before.)

      Zitat von HartmutB Beitrag anzeigen
      I guess, you adjusted the values for minimum, maximum etc. for calibration ?
      After having set the max value to 16m in ETS.... here are the readings from 0 to 4m

      Code:
       
      Read - Meas - Diff
      4        4    0
      2,96     3    0,04
      2        2    0
      0,96     1    0,04

      NB: The small differences might be due to my measuring method not beeing acurate enough. Anyway, I'm confident to drop the thing in the pit.

      Thank you for having spend some time looking at this post.

      PS: I've still an open question, which I submitted to ABB's TechSup, about the way to use the treshold 1&2, upper&lower limit. Seems it's not possible to set a fractional value there , only integers. Heck, makes a difference, between 1 & 2, that's 1.368L in my case. If I had a "zisterne" of 4m, those parameters would be unusable. I have only the german version of the doc, so I'm not quite sure of my understanding.

      Kommentar


        #78
        Fine. Now the probe is working, finally .

        Zitat von Warichet Beitrag anzeigen
        PS: I've still an open question, which I submitted to ABB's TechSup, about the way to use the treshold 1&2, upper&lower limit. Seems it's not possible to set a fractional value there , only integers. Heck, makes a difference, between 1 & 2, that's 1.368L in my case. If I had a "zisterne" of 4m, those parameters would be unusable. I have only the german version of the doc, so I'm not quite sure of my understanding.
        If it wouldn't be you and the german manual version, I would give you a RTFM . But tha't unfair, I know.

        Here is the solution: If 136,8L are exact enough, simply set the "factor for output threshold" to "0,1" in combination with "Output value for upper limit" to "140". You will get the same values in the KO as before, but a change of "1" in the threshold will be 10cm in fact. If you want your threshold between 1,4 and 1,5m, you would have to enter "14" and "15" as tolerance band settings.

        If you need a higher resolution, you will have to use your HS.
        Either make the threshold part with logic there, or use it for "offsetting" your values, as the AE/S still would switch your pump, independing of a working HS (and if the HS is offline: there is no need of a values for the visu...):

        The settings for the output values are limited -1000 .. 1000. If you set the factor to "0,01", you won't be able to get more than 10m (but a resolution of 13,68L at threshold). What you can do is to set the lower output value to (let's say) -400 and the upper to +1000.
        An empty pit will give you "-4m" instead of "0m" and a completly filled pit "+10m" instead of the expected "14m". A simple addition in the HS can compensate for this, you could still use the threshold mechanism in the AE/S to check for limits. According to the above example of 1,4 and 1,5m, you would have to set the threshold parameters to -400 + 140 = -260 and -400 + 150 = -250.


        Regards,
        Hartmut

        BTW: "Apfelwein": Which region of Germany, has it been Hessen ? What cities in the neighborhood ?

        Kommentar


          #79
          Zitat von HartmutB Beitrag anzeigen
          If it wouldn't be you and the german manual version, I would give you a RTFM .
          You are too nice with the dummies

          Zitat von HartmutB Beitrag anzeigen
          Here is the solution: If 136,8L are exact enough, simply set the "factor for output threshold" to "0,1" in combination with "Output value for upper limit" to "140". You will get the same values in the KO as before, but a change of "1" in the threshold will be 10cm in fact. If you want your threshold between 1,4 and 1,5m, you would have to enter "14" and "15" as tolerance band settings.
          ûûh, clever and all this in the manual

          Zitat von HartmutB Beitrag anzeigen
          If you need a higher resolution, you will have to use your HS.
          Either make the threshold part with logic there, or use it for "offsetting" your values, as the AE/S still would switch your pump, independing of a working HS.
          Great, thank you for the tip.

          Zitat von HartmutB Beitrag anzeigen
          The settings for the output values are limited -1000 .. 1000. If you set the factor to "0,01", you won't be able to get more than 10m .
          Guess what, if you hadn't told me, I'd have tried that alternative .... just to bump into the limitation you mention.

          A resolution of 136L is fine for a domestic usage, so I'll keep it simple .

          As an aside .... I want to display the status of the AE/A in clear text in the Visu. I've already done something similar for a thermostat, using a Baustein "1 Byte to 8 bit" and then assigning the appropriate text to each bit. A bit clumsy, not very elegant. Do you know such a Baustein ? I haven't seen it, I guess I've to write it.

          Zitat von HartmutB Beitrag anzeigen
          "Apfelwein": Which region of Germany
          Rödelheim, west side of FFM

          Kommentar


            #80
            Regarding the status-display, I use a Kurvenfunktion (2Punkte) E1 your value in meters then 0,0,14(your max. height),100(%) or adjust the minimum as needed (I did this as I cannot use the last 30cm with the pump.

            Makki
            EIB/KNX & WireGate & HS3, Russound,mpd,vdr,DM8000, DALI, DMX
            -> Bitte KEINE PNs!

            Kommentar


              #81
              Durch den anderen Thread habe ich da mal wieder gelesen. Wenn das Filterthema noch ungelöst ist, dann meine - nach der Installation des Sensors zugegebenermassen das erste mal in Augenschein genommene - Zisternenlösung.

              Da ich das Wasser nutze für
              * Gartn
              * Waschmaschine
              * Toiletten

              habe ich mich entschlossen, das ungefiltert zu tun. Die einzige und meiner Meinung nach gute Filterung ist bei mir Schwerkraftabhängig.

              Meine Wasserentnahme findet ca. 10 CM unter der Oberfläche statt, das Grobsieb hängt an einem Schwimmer. Die Schwebstoffe setzen sich nach unten ab, so ist das relativ sauber. Die Pumpe wurschtet alles angesaugte durch. Mal nachgesehen, ist auf der WILO - HP ordentlich beschrieben und abgebildet.

              Nach 2 Jahre habe ich jetzt mittels eines Wassersaugers die abgelagerten Schwebstoffe mal rausgesaugt, das wars.

              Übrigens, bevor einer da auf schlechte Gedanken kommt, meine weißen hemden sind noch Blütenweiss, mit Ausnahme der Tomatensauce, aber für die kann ja die Zisterne nix. ;-)
              never fummel a running system...

              Kommentar


                #82
                Moin,
                kann mir hier mal bitte einer die Tomaten von den Klüsen nehmen?

                Weder hier im Forum noch bei Prignitz finde/sehe ich etwas von der Ader Belegung bei dem Sensor.

                Bei

                weiß = GND
                braun = 24V
                gelb/gruen = Sensor

                bekomme ich keine Werte und zum zerschiessen ist mir das Ding etwas zu teuer.
                cu
                Andreas


                Aus dem Norden? Schau mal rein, Stammtisch-Nord!

                Kommentar


                  #83
                  Zitat von arosy Beitrag anzeigen
                  weiß = GND
                  braun = 24V
                  gelb/gruen = Sensor
                  ûûh
                  My Prignitz connection

                  Prignitz white -> +24V DC power supply
                  Prignitz brown -> A of the A/D converter (in my case ABB AE/A 2.1)
                  Prignitz gelb/gruen, not connected

                  ABB AE/A 0V -> -24V DC power supply

                  So, the sensor & the AD converter are serial with the power supply

                  Kommentar


                    #84
                    Zitat von Warichet Beitrag anzeigen
                    Prignitz white -> +24V DC power supply
                    Prignitz brown -> A of the A/D converter (in my case ABB AE/A 2.1)
                    Thanks, there is a real Response.

                    Zitat von Warichet Beitrag anzeigen
                    Prignitz gelb/gruen, not connected
                    But now there's a litle bit confusion. Why does this is a three wire version?
                    cu
                    Andreas


                    Aus dem Norden? Schau mal rein, Stammtisch-Nord!

                    Kommentar


                      #85
                      Zitat von arosy Beitrag anzeigen
                      Thanks, there is a real Response.
                      OK, can you send me the "Tomaten" please


                      Zitat von arosy Beitrag anzeigen
                      Why does this is a three wire version?
                      If you look at the sensor itself, at the bottom, there is a small label with tiny writing for the connexion.
                      But you are right, they could include a piece of paper with the minimum details for installation.

                      Kommentar


                        #86
                        Hallo,

                        ich habe heute meine Pegelsonde von Prignitz erhalten.
                        Mich würde jetzt intressieren, ob ihr ein zusätzliches Gewicht angebracht habt, das die Sonde nach unten zieht?
                        Angeschloßen wird braun und weiß?

                        Gruß
                        Markus
                        Meine Installation: Home Server 3.0, Microvis II logic , Controlpanel 6136/100M, Info Display V2.0, Plantec 18F mit Display, Buderus FM446, Siemens-LOGO, Elsner Helligkeitgeber u.Globalstrahlungssensor,Merten Muf mit RTR; usw.

                        Kommentar


                          #87
                          Hallo Markus,

                          nachdem die Sonde ansich schon nicht so leicht ist habe ich die einfach ohne zusätzliches Gewicht reingehängt! Funktioniert seit längerem super, ohne ausfälle!

                          Gruß Jochen

                          Kommentar


                            #88
                            Sorry ich vergaß, richtig angeschlossen wird braun / weiß!

                            Jochen

                            Kommentar


                              #89
                              Danke, für deinen Beitrag.

                              Gruß
                              Markus
                              Meine Installation: Home Server 3.0, Microvis II logic , Controlpanel 6136/100M, Info Display V2.0, Plantec 18F mit Display, Buderus FM446, Siemens-LOGO, Elsner Helligkeitgeber u.Globalstrahlungssensor,Merten Muf mit RTR; usw.

                              Kommentar


                                #90
                                die sonde liegt bei mir auf dem Zisternenboden, ist wichtig, daß sie ganz absinkt. Ein extra Gewicht braucht das nicht!
                                never fummel a running system...