    [OT] Recomendation about Reed switch

    Hi,

    Anyone having a recomendation about high quality, reliable Reed switch ?

    I've already installed some of those devices, but they tend to have problems after a year or so. Usually, the contacts stick together although they have been installed according to manufacturer specifications about the distance between the magnet and the contact. I'm looking for the classical On/Off Reed (not the impedance loaded)

    Thank you

    #2
    Hello Raymond,
    I've no recommendation about reed contacts for you.
    But I think you should have a look at the rest of your installation.
    A to high voltage during switching can lead to arcing during switching. In consequence the contacts will stick together.
    There are to main issues that will prevent arcing in the reed.
    - short wire length between reed contact and binary input device
    - low voltage
    Some binary input devices have a very low voltage of 5V or even 3.3V and are best to prevent arcing. I've heard also about some devices which should pulse the current.

    Arcing is connected with long wire lenght because of the very fast switching of a reed contact and the fast discharge of capacity (or inductivity, I don't know excactly) on the wire.

    Greetings, Sebastian
    Baustelle 2.0 (Detailprogrammierung und Restarbeiten)
    Ruhri? -> Komm zum Stammtisch

    Kommentar


      #3
      Hi Sebastian,

      Zitat von Bainit Beitrag anzeigen
      A to high voltage during switching can lead to arcing during switching.
      Thank you for bringing this isue to my attention.
      I should have given a bit more information, all Reed are connected via ABB or Merten 4 fold or ABB UK/S binary inputs, I guess the voltage should not be an issue as it is pulsed from the BE.

      Zitat von Bainit Beitrag anzeigen
      Arcing is connected with long wire lenght because of the very fast switching of a reed contact and the fast discharge
      Unfortunately, the wire length is not an adjustable parameter, indeed I've some lengths of 30m (I've seen reports where someone tested a coil of 100m KNX cable with a binary input, no problem, although no idea about long time testing results)

      Kommentar


        #4
        Zitat von Warichet Beitrag anzeigen
        I guess the voltage should not be an issue as it is pulsed from the BE.
        Hey Raymond,

        I don't know for the Merten, but I doubt this for the ABB UK/S. The BE/S 4.20.1 should have a pulsed voltage.

        AFAIK, you need to provide the contact voltage by yourself ... so do you use 24 or 12 V?

        Cheers,

        Stefan
        Mein Sammelsurium: TS2, Zennio Z38, Siemens LOGO!, Medeodata 140 S, Weinzierl KNX ENO 620, Eibmarkt IP Router, MDT KNX IP IF, Wiregate, Node-Red mit KNX Ultimate, MDT Smart II, diverse Aktoren verschiedener Hersteller ...

        Kommentar


          #5
          Hi Stefan,

          Zitat von lobo Beitrag anzeigen
          I doubt this for the ABB UK/S.
          You are right for the UK/S I did indeed supply an external 24 V.
          Do you think this might be to high a voltage for the Reed lifetime ?

          Kommentar


            #6
            Raymond,

            as far as I know, there are much more differenzes between the different possibilities to read out the reed-relays than in the relays themselves, so as Sebastian already proposed, better have a close look onto your electrical read-out.

            24 V is a fairly high value ... although the given values for the allowed voltage for reeds is often significantly higer, you will get quite some trouble concerning the stored charges within your cable. There were several posts concerning this issu from StefanW (I just foundthis one).

            So - my understanding would be to first look for a reed that can withstand as much voltage as possible and in the long run you should perhaps have a look onto the MDT Binary inputs. As far as I remember, they do have a fairly low pulsed voltage and they allow cable lenths up to 100 m.

            Best regards,

            Stefan
            Mein Sammelsurium: TS2, Zennio Z38, Siemens LOGO!, Medeodata 140 S, Weinzierl KNX ENO 620, Eibmarkt IP Router, MDT KNX IP IF, Wiregate, Node-Red mit KNX Ultimate, MDT Smart II, diverse Aktoren verschiedener Hersteller ...

            Kommentar


              #7
              Hello,
              I'm absolutely agree with Stefan's statement.
              But I want to add, that it could help to change your power souce from 24V to 12 V before switching from ABB UK/S to MDT. Does the UK/S has dedicated power sources for contacts and own power supply? In this case it could be interesting to try switching from 24 V to only 5V.

              Greetings, Sebastian
              Baustelle 2.0 (Detailprogrammierung und Restarbeiten)
              Ruhri? -> Komm zum Stammtisch

              Kommentar


                #8
                @Stefan
                Zitat von lobo Beitrag anzeigen
                24 V is a fairly high value ... although the given values for the allowed voltage for reeds is often significantly higer, you will get quite some trouble concerning the stored charges within your cable.
                OK, fine
                Zitat von lobo Beitrag anzeigen
                There were several posts concerning this issu from StefanW
                Thank you for the pointer, interesting reading.

                @Sebastian
                Zitat von Bainit Beitrag anzeigen
                it could help to change your power souce from 24V to 12 V
                OK, point taken.
                Zitat von Bainit Beitrag anzeigen
                Does the UK/S has dedicated power sources for contacts and own power supply?
                No, it's a multipurpose power supply, also used for devices needing external power, but no problem to add/change if required.
                Zitat von Bainit Beitrag anzeigen
                In this case it could be interesting to try switching from 24 V to only 5V.
                5V ?!? but that's outside the specs of the UK/S. Any experience with a UK/S running 5V on the Reeds ? no negative effect on distance ?