This isn't working as I expect. First let me check something.
You show a E4 node+ here which in earlier diagrams is connected to RunStatus output of velux main. Is that correct?
Also what does E5 node+0 do? It seems to select between the frame sent at the start or the frame sent at the end of movement. Correct?
So I connected things up as show, using only a single GW_COMMAND_RUN_STATUS_NTF to keep it simple.
I request Open - Window starts opening - No Feedback
I request Stop when window is halfway - Window stops - No Feedback
I request Stop - Window static - I receive feedback which looks correct
I request close - window closes all the way - No Feedback
I request Stop - Window static - No Feedback
I request Stop - Window static - Feedback indicates closed
It's as if the feedback is a couple of commands behind.
Also I do not get any feedback when operated from remote. HMon is on and I see the commands logged from the gateway but they are not Run Status notification which is maybe why they are not picked up by the logic node.
I have attached my logic diagram and csv output of what I described above in case it helps.
I noticed you have some sort of log archive in place. Is this one of the stands HS nodes? Where can I get it?
Many thanks,
Tas
You show a E4 node+ here which in earlier diagrams is connected to RunStatus output of velux main. Is that correct?
Also what does E5 node+0 do? It seems to select between the frame sent at the start or the frame sent at the end of movement. Correct?
So I connected things up as show, using only a single GW_COMMAND_RUN_STATUS_NTF to keep it simple.
I request Open - Window starts opening - No Feedback
I request Stop when window is halfway - Window stops - No Feedback
I request Stop - Window static - I receive feedback which looks correct
I request close - window closes all the way - No Feedback
I request Stop - Window static - No Feedback
I request Stop - Window static - Feedback indicates closed
It's as if the feedback is a couple of commands behind.
Also I do not get any feedback when operated from remote. HMon is on and I see the commands logged from the gateway but they are not Run Status notification which is maybe why they are not picked up by the logic node.
I have attached my logic diagram and csv output of what I described above in case it helps.
I noticed you have some sort of log archive in place. Is this one of the stands HS nodes? Where can I get it?
Many thanks,
Tas